buildingdoc
Full Access Members
It is true... most manufacturers do slightly undercharge... an oz per car can save a ton in the long run. But I don't think the problem is an undercharge issue. If so, you would have a lower suction pressure.
Your accumulator has two purposes. It boils off any remaining liquid refrigerant so that only vapor returns to the compressor. It should also contain a white or grey sack of desiccant that absorbs moisture because moisture and refrigerant create hydrofluoric acid that will eat up your seals from the inside out.
The condenser... it is a parallel flow condenser (old style was tube and fin). If your last condenser did have a catastrophic failure I would urge anyone to replace the condenser if you have a parallel flow. It is impossible to flush out. But at 90* and 230 on the high side... sounds like you are getting proper cooling at the condenser. Best way to confirm is get a temp in and out and you should see about a 20 degree drop. Also carefully take temps on the refrigerant lines between the condenser and the expansion valve to make sure the temp is consistent. If you notice a rapid drop in temp, that is a restriction.
This is a tough one. Have you checked to make sure the hot water valve is closing and not allowing any warm coolant to enter into the heater core? This is where experience really comes in and having hands on would tell the story much better.
Your accumulator has two purposes. It boils off any remaining liquid refrigerant so that only vapor returns to the compressor. It should also contain a white or grey sack of desiccant that absorbs moisture because moisture and refrigerant create hydrofluoric acid that will eat up your seals from the inside out.
The condenser... it is a parallel flow condenser (old style was tube and fin). If your last condenser did have a catastrophic failure I would urge anyone to replace the condenser if you have a parallel flow. It is impossible to flush out. But at 90* and 230 on the high side... sounds like you are getting proper cooling at the condenser. Best way to confirm is get a temp in and out and you should see about a 20 degree drop. Also carefully take temps on the refrigerant lines between the condenser and the expansion valve to make sure the temp is consistent. If you notice a rapid drop in temp, that is a restriction.
This is a tough one. Have you checked to make sure the hot water valve is closing and not allowing any warm coolant to enter into the heater core? This is where experience really comes in and having hands on would tell the story much better.